CR1000 manual suggest DSP4, and GOESData functions as alternatives to store data besides a card. In loggernet there is not further reference for DSP4; I followed the instructions for the use of GOESData (see code below) but I wasn't successful. Can somebody please post an example of the use of those instructions and what are the devices needed to use the GOES functionality?
Thank you very much!
'CR1000
' The following sample program makes a few simple measurements of leaf wetness sensor and store them in the table named LWS.
'Declare Variables and Units
Public BattV
Public LWmV
Public LWMDry
Public LWMCon
Public LWMWet
Dim SATData
Dim SATStatus(13)
Units BattV=Volts
Units LWmV=mV
Units LWMDry=Minutes
Units LWMCon=Minutes
Units LWMWet=Minutes
'Define Data Tables
DataTable(lws,True,-1)
	DataInterval(0,1,Min,10)
	Minimum(1,BattV,FP2,False,False)
	Sample(1,LWmV,FP2)
	Maximum(1,LWmV,FP2,False,True)
	Totalize(1,LWMDry,FP2,False)
	Totalize(1,LWMCon,FP2,False)
	Totalize(1,LWMWet,FP2,False)
EndTable
'Main Program
BeginProg
	Scan(5,Sec,1,0)
		'Default Datalogger Battery Voltage measurement BattV
		Battery(BattV)
		'LWS Dielectric Leaf Wetness Sensor measurement LWmV
		BrHalf(LWmV,1,mV2500,1,1,1,2500,False,10000,_60Hz,2500,0)
		'Determine Minutes Dry (LWMDry), Minutes Wet or Contaminated (LWMCon), and Minutes Wet (LWMWet) for this Scan
		LWMDry=0
		LWMCon=0
		LWMWet=0
		If LWmV<274 Then
			LWMDry=0.08333333
		Else
			If LWmV>=284 Then
				LWMWet=0.08333333
			Else
				LWMCon=0.08333333
			EndIf
		EndIf
		'Call Data Tables and Store Data
		CallTable(lws)
		'==== All new data from this table is transmitted hourly. 
		If TimeIntoInterval (0,1,Hr)
       GOESData (SATData,lws,0,0,1)
      EndIf
      If TimeIntoInterval (0,1,Day)
       GOESStatus (SATStatus,1)
      EndIf
The GOESData instruction is something that is only used if you have a satellite data transmitter.
If you are looking for alternatives to using an NL115 or CFM100 and storing data to a card, you might want to look at our SC115. It works with any of our dataloggers that has a CS I/O port:
http://www.campbellsci.com/sc115
Regards, Dana