Our full technical support staff does not monitor this forum. If you need assistance from a member of our staff, please submit your question from the Ask a Question page.


Log in or register to post/reply in the forum.

VoltSE datable values


MHyatt Nov 17, 2025 08:51 PM

I am using a 3:1 voltage divider to allow reading of a 9 to15volt DC input to U2. (provides 3 to 5volts to U2).  The varible I use shows the correct scaled value.  VoltSe(POEV,1,mV5000,U2,False,500,5,Mult(2),Offs(2)) - this work fine.

For the data table I have:

DataTable(POEVout,True,-1)

DataInterval(0,10,Sec,2)

FieldNames("POEBV") 

Median(1,POEV,10,FP2,False)

EndTable

The issue is the value in the datatable rails at 7999mV, so I cannot capture any voltage over 8volts (which with a 3:1 divider is only 2.666v applied to U2.

thoughts?

Matt


JDavis Nov 17, 2025 09:12 PM

I believe the issue is your data table. Change the output data type from FP2 to IEEE4.


MHyatt Nov 18, 2025 10:29 AM

This post is under review.

Log in or register to post/reply in the forum.