Hello,
I'm dealing with a Modbus problem for a digital barometer. I'm using a CR6 and this barometer:
https://www.baranidesign.com/meteopressure-msb181
It talks in serial with 9600 baud, no parity, and 8 databits.
The pressure is on Register 24 ( 32bit float) little endian. (DCBA).
Terminal string example:
01 03 0018 0002 7687
where 
01 - address of the device
03 - function code 03
0018 - starting register ( 24DEC = 18Hex)0002 - count of registers to be read out ( here 2x 16 bit)
7687 - CRC
Here's the modbusmaster function I've created for the program:
ModbusMaster (ResultPressure,ComC1,9600,1,3,ModbusDataPressure(),25,1,3,1000)
The terminal is showing this output which looks correct:
10:59:00.000 T 01 03 00 18 00 02 44 0C ......D.
10:59:00.031 R 01 03 04 92 ED 7D 44 67 DD .....}Dg.
And I'm getting the value 1.632812E37. I believe I need to convert this value with MoveBytes.
Any help with this would be great. Thanks!
Bump
SOLVED!
Here's the movebyte function that I used to parse the data:
Sub RunBaraniBarometer()
  ModbusMaster (ResultPressure,ComC1,9600,1,3,ModbusDataPressure(),25,1,3,1000,2)
EndSub
Sub BigtoLittle()
  'converts modbus output to decimal readable values
  MoveBytes (InverseModbusDataPressure(1),3,ModbusDataPressure(1),0,1)
  MoveBytes (InverseModbusDataPressure(1),2,ModbusDataPressure(1),1,1)
  MoveBytes (InverseModbusDataPressure(1),1,ModbusDataPressure(1),2,1)
  MoveBytes (InverseModbusDataPressure(1),0,ModbusDataPressure(1),3,1)
EndSub
Because pressure output of the Barani is two bytes I used the next command that worked fine for me:
ModbusMaster(ModbusResult1,32,19200,1,4,Modbus1(),1,5,1,100,3)
'32 used for SDMIO in RS485 mode on CR1000
then value in mBar:
 If Modbus1(4) = 1 Then val = 65536 Else val = 0
 AirPress = (Modbus1(3) + val)/100
finally I added elevation correction:
 elevation_cor = 1013.25 * (1 - (1 -elevation/44307.69231)^5.253283)
 Airpress_cor = AirPress + elevation_cor
maybe it helps playing with modbus