Our full technical support staff does not monitor this forum. If you need assistance from a member of our staff, please submit your question from the Ask a Question page.


Log in or register to post/reply in the forum.

Totalize Invalid


Shanks.J Dec 18, 2018 05:48 PM

when trying to upload a new simple cod to the CR6 

lines below are seen as invalid "totalize" is not recognised as a comand!

please advise on how to make this work. am trying to total rainfall over a set period.


'########## Define Data Tables ##########
DataTable(Table1,True,-1)
DataInterval(0,10,Min,10) 'write table every 10 minutes
Sample (1,LoggerName,String)
Sample (1,SupplyVolts,FP2)
Sample (1,LithiumVolts,FP2)
Sample (1,PTemp_degC,FP2)
Totalize (1,Rain1_mm,FP2)
Totalize (1,Rain2_mm,FP2)
Average (1,nmbr_satellites,FP2,False)
Sample (1,latitude_a,String)
Sample (1,latitude_b,String)
Sample (1,longitude_a,String)
Sample (1,longitude_b,String)
Sample (1,speed,String)
Sample (1,course,String)
Sample (1,altitude,String)

'##########  Main Program  ###########BeginProg  LoggerName="FoxLandslide" 'ie a unique name for this logger  'Main Scan  Scan(1,Min,1,0) 'Scan once every minute    Battery(Batt_volt())'Read the supply and lithium voltages    PanelTemp(PTemp_degC,50) 'Read CR6 internal temp    PulseCount(Rain1_mm,1,U1,2,0,0.2,0) 'Read the 0.2mm TB3 Rain Gauge    PulseCount(Rain2_mm,1,U2,2,0,1,0) 'Read the 1mm TB3 Rain Guage    CallTable Table1  'Call Data Table and Store Data
  NextScan


nsw Jan 2, 2019 04:37 AM

Much of your programn is missing from the above listing.

Are you using CRBasic to create this program? If you are, then when you compile it, CRBasic will list many errors that you will need to rectify.

I think the CR6 is rejecting the program as there are many things wrong with it.

You will need CRBasic to write this program for the CR6. Or you use ShortCut instead, which you can get from the Campbell Scientific website.

Log in or register to post/reply in the forum.