Our full technical support staff does not monitor this forum. If you need assistance from a member of our staff, please submit your question from the Ask a Question page.


Log in or register to post/reply in the forum.

Integrating Navcom SF3040 GPS with CR1000 datalogger


Phenomics Nov 13, 2017 09:09 PM

Hello.

I am having some trouble integrating a Navcom SF3040 with a CR1000 datalogger. I am getting some NMEA string data but it is very intermittent. I have attached the program below plus attached the

Current two issues:

1. To get any NMEA data recorded, I have to start the CR1000 program and then switch on the Navcom unit. I did add a serialflush command to try and rectify this, without any success. Any suggestions?

2. The NMEA string data is recording for about thirty seconds and then becomes static (same NMEA string repeating for 30-90 seconds). How do I solve this?

***********program***************

Const GPSPort = Com1 'Com port where GPS is connected

Public GGAstring As String * 500

Public RMCstring As String * 500

'rmc variables

Public rmcid As String

Public rmcutc As String

Public rmcstatus As String

Public rmclatitude As String

Public rmcin_s_ind As String

Public rmclongitude As String

Public rmce_w_indicator As String

Public rmcspeed As String

Public rmccourse As String

Public rmcutcdate As String

Public rmcmagvariation As String

Public rmcmage_w As String

Public rmcchecksum As String

'gga variables

Public ggaid As String

Public ggautc As String

Public ggailatitude As String

Public ggan_s_ind As String

Public ggalongitude As String

Public ggae_w_ind As String

Public ggapositionfix As String

Public gganumsatellites As String

Public ggahdop As String

Public ggaaltitude As String

Public ggaaltutudeunits As String

Public ggageoidsep As String

Public ggageoidunits As String

Public ggachecksum As String

Dim NBytesReturned As Long

Dim SubStrings(16) As String * 32, rawdata As String * 500

Dim CalculatedChecksum As Long, ReportedChecksum As Long

 

 

DataTable (gpsdata,True,-1)

  CardOut(0,144000) '8 hours at 5Hz

' DataInterval (0,1,Sec,10) will execute with each program scan call

 Sample (1,rmcid,String)

 Sample (1,rmcutc,String)

 Sample (1,rmcstatus,String)

 Sample (1,rmclatitude,String)

 Sample (1,rmcin_s_ind,String)

 Sample (1,rmclongitude,String)

 Sample (1,rmcspeed,String)

 Sample (1,rmccourse,String)

 Sample (1,rmcutcdate,String)

 Sample (1,rmcmagvariation,String)

 Sample (1,rmcmage_w,String)

 Sample (1,rmcchecksum,String)

 Sample (1,ggaid,String)

 Sample (1,ggautc,String)

 Sample (1,ggan_s_ind,String)

 Sample (1,ggalongitude,String)

 Sample (1,ggae_w_ind,String)

 Sample (1,ggapositionfix,String)

 Sample (1,gganumsatellites,String)

 Sample (1,ggahdop,String)

 Sample (1,ggaaltitude,String)

 Sample (1,ggaaltutudeunits,String)

 Sample (1,ggageoidsep,String)

 Sample (1,ggageoidunits,String)

 Sample (1,ggachecksum,String)

EndTable

 

BeginProg

    SerialOpen (GPSPort,19200,3,0,1001)'reduced buffer sizes, should be plenty big

   SerialFlush(GPSPort)

Scan (100,mSec,0,0)

     SerialInRecord (GPSPort,rawdata,36,0,&h0D0A,NBytesReturned,11)

     CalculatedChecksum = CheckSum (rawdata,9,Len(rawdata) - 3)

     CalculatedChecksum = CalculatedChecksum AND 255

     ReportedChecksum = HexToDec(Right(rawdata,2))

     If CalculatedChecksum = ReportedChecksum Then

     If InStr (1,rawdata,"GPRMC",2) Then

     RMCstring = rawdata

     ElseIf InStr (1,rawdata,"GPGGA",2) Then

     GGAstring = rawdata

     EndIf

     Endif

    'parse rmc data

     SplitStr (SubStrings(),RMCstring,",",16,5)

     rmcid = SubStrings(1)

     rmcutc = SubStrings(2)

     rmcstatus = SubStrings(3)

     rmclatitude = SubStrings(4)

     rmcin_s_ind =SubStrings(5)

     rmclongitude=SubStrings(6)

     rmce_w_indicator=SubStrings(7)

     rmcspeed=SubStrings(8)

     rmccourse=SubStrings(9)

     rmcutcdate=SubStrings(10)

     rmcmagvariation=SubStrings(11)

     rmcmage_w =Left(SubStrings(12),1)

     rmcchecksum=Right(RMCstring,2)

     'parse gga Data

     SplitStr (SubStrings(),GGAstring,",",16,5)

     ggaid=SubStrings(1)

     ggautc=SubStrings(2)

     ggailatitude=SubStrings(3)

     ggan_s_ind=SubStrings(4)

     ggalongitude=SubStrings(5)

     ggae_w_ind=SubStrings(6)

     ggapositionfix=SubStrings(7)

     gganumsatellites=SubStrings(8)

     ggahdop=SubStrings(9)

     ggaaltitude=SubStrings(10)

     ggaaltutudeunits=SubStrings(11)

     ggageoidsep=SubStrings(12)

     ggageoidunits=Left(SubStrings(13),1)

     ggachecksum=Right(GGAstring,2)

 

 CallTable gpsdata

 NextScan

EndProg

************************************SAMPLE DATA*******************************

14/11/2017 13:3039GPRMCV29GPGGA0MM6614/11/2017 13:3040GPRMCV29GPGGA0MM6614/11/2017 13:3041GPRMCV29GPGGA0MM6614/11/2017 13:3042GPRMCV29GPGGA0MM6614/11/2017 13:3043GPRMCV29GPGGA0MM6614/11/2017 13:3044GPRMCV29GPGGA0MM6614/11/2017 13:3045GPRMCV29GPGGA0MM6614/11/2017 13:3046GPRMCV29GPGGA0MM6614/11/2017 13:3047GPRMCV29GPGGA0MM6614/11/2017 13:3048GPRMCV29GPGGA0MM6614/11/2017 13:3049GPRMCV29GPGGA0MM6614/11/2017 13:3050GPRMCV29GPGGA0MM6614/11/2017 13:3051GPRMCV29GPGGA0MM6614/11/2017 13:3052GPRMCV29GPGGA0MM6614/11/2017 13:3053GPRMCV29GPGGA0MM6614/11/2017 13:3054GPRMCV29GPGGA0MM6614/11/2017 13:3055GPRMCV29GPGGA0MM6614/11/2017 13:3056GPRMCV29GPGGA0MM6614/11/2017 13:3057GPRMCV29GPGGA0MM6614/11/2017 13:3058GPRMCV29GPGGA0MM6614/11/2017 13:3059GPRMCV29GPGGA0MM6614/11/2017 13:3060GPRMCV29GPGGA0MM6614/11/2017 13:3061GPRMCV29GPGGA0MM6614/11/2017 13:3062GPRMCV29GPGGA0MM6614/11/2017 13:3063GPRMCV29GPGGA0MM6614/11/2017 13:3064GPRMCV29GPGGA0MM6614/11/2017 13:3065GPRMCV29GPGGA0MM6614/11/2017 13:3066GPRMCV29GPGGA0MM6614/11/2017 13:3067GPRMCV29GPGGA0MM6614/11/2017 13:3068GPRMCV29GPGGA0MM6614/11/2017 13:3069GPRMCV29GPGGA0MM6614/11/2017 13:3070GPRMCV29GPGGA0MM6614/11/2017 13:3071GPRMCV29GPGGA0MM6614/11/2017 13:3072GPRMCV29GPGGA0MM6614/11/2017 13:3073GPRMCV29GPGGA0MM6614/11/2017 13:3074GPRMCV29GPGGA0MM6614/11/2017 13:3075GPRMCV29GPGGA0MM6614/11/2017 13:3076GPRMCV29GPGGA0MM6614/11/2017 13:3077GPRMC23056.7A3749.252496S14203.917180.08338.6141117  7GPGGA    0   M M6614/11/2017 13:3078GPRMC23057.7A3749.252178S14203.916780.1116.3141117  7GPGGA    0   M M6614/11/2017 13:3079GPRMC23058.7A3749.252413S14203.916890.13250.2141117  2GPGGA    0   M M6614/11/2017 13:3180GPRMC23059.7A3749.252718S14203.917610.24193.5141117  1GPGGA    0   M M6614/11/2017 13:3181GPRMC23059.7A3749.252718S14203.917610.24193.5141117  1GPGGA    0   M M6614/11/2017 13:3182GPRMC23059.7A3749.252718S14203.917610.24193.5141117  1GPGGA    0   M M6614/11/2017 13:3183GPRMC23059.7A3749.252718S14203.917610.24193.5141117  1GPGGA    0   M M6614/11/2017 13:3184GPRMC23059.7A3749.252718S14203.917610.24193.5141117  1GPGGA    0   M M6614/11/2017 13:3185GPRMC23104.7A3749.252453S14203.91780.14192.1141117  6GPGGA    0   M M6614/11/2017 13:3186GPRMC23105.7A3749.252513S14203.91780.1573.1141117  3DGPGGA    0   M M6614/11/2017 13:3187GPRMC23105.7A3749.252513S14203.91780.1573.1141117  3DGPGGA    0   M M6614/11/2017 13:3188GPRMC23107.7A3749.252592S14203.917670.05140.7141117  6GPGGA    0   M M6614/11/2017 13:3189GPRMC23108.7A3749.252604S14203.917650.24264.9141117  6GPGGA    0   M M6614/11/2017 13:3190GPRMC23108.7A3749.252604S14203.917650.24264.9141117  6GPGGA    0   M M6614/11/2017 13:3191GPRMC23110.7A3749.25259S14203.917630.37211.7141117  3GPGGA    0   M M6614/11/2017 13:3192GPRMC23110.7A3749.25259S14203.917630.37211.7141117  3GPGGA23111.7S14203.9176E145.1214M0M4414/11/2017 13:3193GPRMC23112.7A3749.250829S14203.921860.31254.1141117  1GPGGA23111.7S14203.9176E145.1214M0M4414/11/2017 13:3194GPRMC23113.7A3749.250848S14203.921830.5672.3141117  37GPGGA23111.7S14203.9176E145.1214M0M4414/11/2017 13:3195GPRMC23114.7A3749.250912S14203.921820.17112.6141117  8GPGGA23111.7S14203.9176E145.1214M0M4414/11/2017 13:3196GPRMC23115.7A3749.252159S14203.919320.26219141117  4GPGGA23111.7S14203.9176E145.1214M0M4414/11/2017 13:3197GPRMC23115.7A3749.252159S14203.919320.26219141117  4GPGGA23111.7S14203.9176E145.1214M0M4414/11/2017 13:3198GPRMC23117.7A3749.250724S14203.919090.08285.6141117  0FGPGGA23111.7S14203.9176E145.1214M0M4414/11/2017 13:3199GPRMC23118.7A3749.250823S14203.91910.110.2141117  3CGPGGA23111.7S14203.9176E145.1214M0M4414/11/2017 13:31100GPRMC23119.7A3749.250911S14203.919080.22354.7141117  0AGPGGA23111.7S14203.9176E145.1214M0M4414/11/2017 13:31101GPRMC23120.7A3749.251076S14203.919080.11152.5141117  0FGPGGA23111.7S14203.9176E145.1214M0M4414/11/2017 13:31102GPRMC23121.7A3749.251278S14203.919140.2599.3141117  3EGPGGA23111.7S14203.9176E145.1214M0M4414/11/2017 13:31103GPRMC23122.7A3749.251469S14203.919190.54227.1141117  1GPGGA23111.7S14203.9176E145.1214M0M4414/11/2017 13:31104GPRMC23123.7A3749.251463S14203.919190.09114.6141117  0AGPGGA23111.7S14203.9176E145.1214M0M4414/11/2017 13:31105GPRMC23123.7A3749.251463S14203.919190.09114.6141117  0AGPGGA23111.7S14203.9176E145.1214M0M4414/11/2017 13:31106GPRMC23125.7A3749.251742S14203.919080.17213.8141117  5GPGGA23111.7S14203.9176E145.1214M0M4414/11/2017 13:31107GPRMC23126.7A3749.25187S14203.919040.17288.5141117  0FGPGGA23111.7S14203.9176E145.1214M0M4414/11/2017 13:31108GPRMC23127.7A3749.251903S14203.9190.3228.3141117  32GPGGA23111.7S14203.9176E145.1214M0M4414/11/2017 13:31109GPRMC23127.7A3749.251903S14203.9190.3228.3141117  32GPGGA23111.7S14203.9176E145.1214M0M4414/11/2017 13:31110GPRMC23129.7A3749.25199S14203.918880.45238.2141117  3GPGGA23111.7S14203.9176E145.1214M0M4414/11/2017 13:31111GPRMC23130.7A3749.252167S14203.918780.53244.9141117  4GPGGA23111.7S14203.9176E145.1214M0M4414/11/2017 13:31112GPRMC23131.7A3749.252277S14203.918720.06246.3141117  5GPGGA23111.7S14203.9176E145.1214M0M4414/11/2017 13:31113GPRMC23132.7A3749.25239S14203.918630.37.5141117  0EGPGGA23111.7S14203.9176E145.1214M0M4414/11/2017 13:31114GPRMC23133.7A3749.252604S14203.918540.15353.7141117  5GPGGA23111.7S14203.9176E145.1214M0M4414/11/2017 13:31115GPRMC23134.7A3749.252798S14203.918460.58211.8141117  1GPGGA23111.7S14203.9176E145.1214M0M4414/11/2017 13:31116GPRMC23135.7A3749.253075S14203.91840.05141.5141117  6GPGGA23111.7S14203.9176E145.1214M0M4414/11/2017 13:31117GPRMC23136.7A3749.253167S14203.918130.29184.8141117  0AGPGGA23111.7S14203.9176E145.1214M0M4414/11/2017 13:31118GPRMC23136.7A3749.253167S14203.918130.29184.8141117  0AGPGGA23137.7S14203.9179E145.2218M0M4714/11/2017 13:31119GPRMC23136.7A3749.253167S14203.918130.29184.8141117  0AGPGGA23137.7S14203.9179E145.2218M0M4714/11/2017 13:31120GPRMC23139.7A3749.254022S14203.918230.54211.7141117  0DGPGGA23137.7S14203.9179E145.2218M0M4714/11/2017 13:31121GPRMC23139.7A3749.254022S14203.918230.54211.7141117  0DGPGGA23137.7S14203.9179E145.2218M0M4714/11/2017 13:31122GPRMC23141.7A3749.254336S14203.918210.3110141117  3FGPGGA23137.7S14203.9179E145.2218M0M4714/11/2017 13:31123GPRMC23142.7A3749.254434S14203.91820.27348.4141117  0FGPGGA23137.7S14203.9179E145.2218M0M4714/11/2017 13:31124GPRMC23143.7A3749.254509S14203.918210.1986.1141117  38GPGGA23137.7S14203.9179E145.2218M0M4714/11/2017 13:31125GPRMC23143.7A3749.254509S14203.918210.1986.1141117  38GPGGA23137.7S14203.9179E145.2218M0M4714/11/2017 13:31126GPRMC23145.7A3749.254648S14203.918220.11289.9141117  3GPGGA23137.7S14203.9179E145.2218M0M4714/11/2017 13:31127GPRMC23146.7A3749.254717S14203.918240.5267.5141117  6GPGGA23137.7S14203.9179E145.2218M0M4714/11/2017 13:31128GPRMC23147.7A3749.254766S14203.918230.15105.3141117  13GPGGA23137.7S14203.9179E145.2218M0M4714/11/2017 13:31129GPRMC23148.7A3749.254835S14203.91820.08359.2141117  17GPGGA23137.7S14203.9179E145.2218M0M4714/11/2017 13:31130GPRMC23148.7A3749.254835S14203.91820.08359.2141117  17GPGGA23137.7S14203.9179E145.2218M0M4714/11/2017 13:31131GPRMC23150.7A3749.255049S14203.918130.18203.6141117  10GPGGA23137.7S14203.9179E145.2218M0M4714/11/2017 13:31132GPRMC23151.7A3749.255181S14203.918090.1426.4141117  23GPGGA23137.7S14203.9179E145.2218M0M4714/11/2017 13:31133GPRMC23151.7A3749.255181S14203.918090.1426.4141117  23GPGGA23137.7S14203.9179E145.2218M0M4714/11/2017 13:31134GPRMC23153.7A3749.255496S14203.918020.21178.3141117  1BGPGGA23137.7S14203.9179E145.2218M0M4714/11/2017 13:31135GPRMC23154.7A3749.25567S14203.917980.31196.3141117  1BGPGGA23137.7S14203.9179E145.2218M0M4714/11/2017 13:31136GPRMC23155.7A3749.25584S14203.917950.3152.7141117  24GPGGA23137.7S14203.9179E145.2218M0M4714/11/2017 13:31137GPRMC23156.7A3749.256025S14203.917920.6480.3141117  29GPGGA23137.7S14203.9179E145.2218M0M4714/11/2017 13:31138GPRMC23157.7A3749.256209S14203.91790.5136.6141117  26GPGGA23137.7S14203.9179E145.2218M0M4714/11/2017 13:31139GPRMC23157.7A3749.256209S14203.91790.5136.6141117  26GPGGA23137.7S14203.9179E145.2218M0M4714/11/2017 13:32140GPRMC23157.7A3749.256209S14203.91790.5136.6141117  26GPGGA23137.7S14203.9179E145.2218M0M4714/11/2017 13:32141GPRMC23157.7A3749.256209S14203.91790.5136.6141117  26GPGGA23137.7S14203.9179E145.2218M0M4714/11/2017 13:32142GPRMC23201.7A3749.256895S14203.917780.38187.5141117  11GPGGA23137.7S14203.9179E145.2218M0M4714/11/2017 13:32143GPRMC23202.7A3749.257038S14203.917760.09356.3141117  1EGPGGA23137.7S14203.9179E145.2218M0M4714/11/2017 13:32144GPRMC23203.7A3749.257175S14203.917740.1296.7141117  14GPGGA23137.7S14203.9179E145.2218M0M4714/11/2017 13:32145GPRMC23203.7A3749.257175S14203.917740.1296.7141117  14GPGGA23137.7S14203.9179E145.2218M0M4714/11/2017 13:32146GPRMC23203.7A3749.257175S14203.917740.1296.7141117  14GPGGA23137.7S14203.9179E145.2218M0M4714/11/2017 13:32147GPRMC23206.7A3749.257496S14203.917650.21239.3141117  1AGPGGA23137.7S14203.9179E145.2218M0M4714/11/2017 13:32148GPRMC23206.7A3749.257496S14203.917650.21239.3141117  1AGPGGA23137.7S14203.9179E145.2218M0M4714/11/2017 13:32149GPRMC23208.7A3749.257637S14203.91760.21215.7141117  10GPGGA23137.7S14203.9179E145.2218M0M4714/11/2017 13:32150GPRMC23208.7A3749.257637S14203.91760.21215.7141117  10GPGGA23137.7S14203.9179E145.2218M0M4714/11/2017 13:32151GPRMC23210.7A3749.257738S14203.917550.191.3141117  1BGPGGA23137.7S14203.9179E145.2218M0M4714/11/2017 13:32152GPRMC23210.7A3749.257738S14203.917550.191.3141117  1BGPGGA23137.7S14203.9179E145.2218M0M4714/11/2017 13:32153GPRMC23210.7A3749.257738S14203.917550.191.3141117  1BGPGGA23137.7S14203.9179E145.2218M0M4714/11/2017 13:32154GPRMC23210.7A3749.257738S14203.917550.191.3141117  1BGPGGA23137.7S14203.9179E145.2218M0M4714/11/2017 13:32155GPRMC23214.7A3749.257807S14203.917450.536.2141117  25GPGGA23137.7S14203.9179E145.2218M0M4714/11/2017 13:32156GPRMC23215.7A3749.257802S14203.917430.2627.9141117  2CGPGGA23137.7S14203.9179E145.2218M0M4714/11/2017 13:32157GPRMC23216.7A3749.257807S14203.917410.31210.5141117  10GPGGA23137.7S14203.9179E145.2218M0M4714/11/2017 13:32158GPRMC23217.7A3749.2578S14203.917380.2764.3141117  2CGPGGA23137.7S14203.9179E145.2218M0M4714/11/2017 13:32159GPRMC23217.7A3749.2578S14203.917380.2764.3141117  2CGPGGA23137.7S14203.9179E145.2218M0M4714/11/2017 13:32160GPRMC23219.7A3749.257784S14203.917350.26276.4141117  1CGPGGA23137.7S14203.9179E145.2218M0M4714/11/2017 13:32161GPRMC23220.7A3749.257773S14203.917330.1611.7141117  2FGPGGA23137.7S14203.9179E145.2218M0M4714/11/2017 13:32162GPRMC23221.7A3749.257764S14203.917320.18263.6141117  11GPGGA23137.7S14203.9179E145.2218M0M4714/11/2017 13:32163GPRMC23222.7A3749.257756S14203.917310.06119.2141117  1CGPGGA23137.7S14203.9179E145.2218M0M4714/11/2017 13:32164GPRMC23223.7A3749.257748S14203.91730.35224.8141117  1DGPGGA23137.7S14203.9179E145.2218M0M4714/11/2017 13:32165GPRMC23224.7A3749.257738S14203.91730.3551.4141117  20GPGGA23137.7S14203.9179E145.2218M0M4714/11/2017 13:32166GPRMC23225.7A3749.257733S14203.917290.31264.5141117  1AGPGGA23137.7S14203.9179E145.2218M0M4714/11/2017 13:32167GPRMC23226.7A3749.257725S14203.917290.5740.9141117  26GPGGA23137.7S14203.9179E145.2218M0M4714/11/2017 13:32168GPRMC23227.7A3749.257722S14203.917280.03308.9141117  11GPGGA23137.7S14203.9179E145.2218M0M4714/11/2017 13:32169GPRMC23228.7A3749.257708S14203.917280.17212.9141117  18GPGGA23137.7S14203.9179E145.2218M0M4714/11/2017 13:32170GPRMC23229.7A3749.257709S14203.917270.11336.7141117  16GPGGA23137.7S14203.9179E145.2218M0M4714/11/2017 13:32171GPRMC23230.7A3749.257701S14203.917250.04244.8141117  12GPGGA23137.7S14203.9179E145.2218M0M4714/11/2017 13:32172GPRMC23231.7A3749.25769S14203.917250.1944.9141117  21GPGGA23137.7S14203.9179E145.2218M0M4714/11/2017 13:32173GPRMC23231.7A3749.25769S14203.917250.1944.914111721GPGGA23137.7S14203.9179E145.2218M0M4714/11/2017 13:32174GPRMC23231.7A3749.25769S14203.917250.1944.914111721GPGGA23137.7S14203.9179E145.2218M0M4714/11/2017 13:32175GPRMC23231.7A3749.25769S14203.917250.1944.914111721GPGGA23137.7S14203.9179E145.2218M0M4714/11/2017 13:32176GPRMC23231.7A3749.25769S14203.917250.1944.914111721GPGGA23137.7S14203.9179E145.2218M0M4714/11/2017 13:32177GPRMC23231.7A3749.25769S14203.917250.1944.914111721GPGGA23137.7S14203.9179E145.2218M0M4714/11/2017 13:32178GPRMC23231.7A3749.25769S14203.917250.1944.914111721GPGGA23137.7S14203.9179E145.2218M0M4714/11/2017 13:32179GPRMC23231.7A3749.25769S14203.917250.1944.914111721GPGGA23137.7S14203.9179E145.2218M0M4714/11/2017 13:32180GPRMC23231.7A3749.25769S14203.917250.1944.914111721GPGGA23137.7S14203.9179E145.2218M0M4714/11/2017 13:32181GPRMC23231.7A3749.25769S14203.917250.1944.914111721GPGGA23137.7S14203.9179E145.2218M0M4714/11/2017 13:32182GPRMC23231.7A3749.25769S14203.917250.1944.914111721GPGGA23137.7S14203.9179E145.2218M0M4714/11/2017 13:32183GPRMC23231.7A3749.25769S14203.917250.1944.914111721GPGGA23137.7S14203.9179E145.2218M0M4714/11/2017 13:32184GPRMC23231.7A3749.25769S14203.917250.1944.914111721GPGGA23137.7S14203.9179E145.2218M0M4714/11/2017 13:32185GPRMC23231.7A3749.25769S14203.917250.1944.914111721GPGGA23137.7S14203.9179E145.2218M0M4714/11/2017 13:32186GPRMC23231.7A3749.25769S14203.917250.1944.914111721GPGGA23137.7S14203.9179E145.2218M0M4714/11/2017 13:32187GPRMC23231.7A3749.25769S14203.917250.1944.914111721GPGGA23137.7S14203.9179E145.2218M0M4714/11/2017 13:32188GPRMC23231.7A3749.25769S14203.917250.1944.914111721GPGGA23137.7S14203.9179E145.2218M0M4714/11/2017 13:32189GPRMC23231.7A3749.25769S14203.917250.1944.914111721GPGGA23137.7S14203.9179E145.2218M0M4714/11/2017 13:32190GPRMC23231.7A3749.25769S14203.917250.1944.914111721GPGGA23137.7S14203.9179E145.2218M0M4714/11/2017 13:32191GPRMC23231.7A3749.25769S14203.917250.1944.914111721GPGGA23137.7S14203.9179E145.2218M0M4714/11/2017 13:32192GPRMC23231.7A3749.25769S14203.917250.1944.914111721GPGGA23137.7S14203.9179E145.2218M0M4714/11/2017 13:32193GPRMC23231.7A3749.25769S14203.917250.1944.914111721GPGGA23137.7S14203.9179E145.2218M0M4714/11/2017 13:32194GPRMC23231.7A3749.25769S14203.917250.1944.914111721GPGGA23137.7S14203.9179E145.2218M0M4714/11/2017 13:32195GPRMC23231.7A3749.25769S14203.917250.1944.914111721GPGGA23137.7S14203.9179E145.2218M0M4714/11/2017 13:32196GPRMC23231.7A3749.25769S14203.917250.1944.914111721GPGGA23137.7S14203.9179E145.2218M0M4714/11/2017 13:32197GPRMC23231.7A3749.25769S14203.917250.1944.914111721GPGGA23137.7S14203.9179E145.2218M0M4714/11/2017 13:32198GPRMC23231.7A3749.25769S14203.917250.1944.914111721GPGGA23137.7S14203.9179E145.2218M0M4714/11/2017 13:32199GPRMC23231.7A3749.25769S14203.917250.1944.914111721GPGGA23137.7S14203.9179E145.2218M0M4714/11/2017 13:33200GPRMC23231.7A3749.25769S14203.917250.1944.914111721GPGGA23137.7S14203.9179E145.2218M0M4714/11/2017 13:33201GPRMC23231.7A3749.25769S14203.917250.1944.914111721GPGGA23137.7S14203.9179E145.2218M0M4714/11/2017 13:33202GPRMC23231.7A3749.25769S14203.917250.1944.914111721GPGGA23137.7S14203.9179E145.2218M0M4714/11/2017 13:33203GPRMC23231.7A3749.25769S14203.917250.1944.914111721GPGGA23137.7S14203.9179E145.2218M0M4714/11/2017 13:33204GPRMC23231.7A3749.25769S14203.917250.1944.914111721GPGGA23137.7S14203.9179E145.2218M0M4714/11/2017 13:33205GPRMC23231.7A3749.25769S14203.917250.1944.914111721GPGGA23137.7S14203.9179E145.2218M0M4714/11/2017 13:33206GPRMC23231.7A3749.25769S14203.917250.1944.914111721GPGGA23137.7S14203.9179E145.2218M0M4714/11/2017 13:33207GPRMC23231.7A3749.25769S14203.917250.1944.914111721GPGGA23137.7S14203.9179E145.2218M0M4714/11/2017 13:33208GPRMC23231.7A3749.25769S14203.917250.1944.914111721GPGGA23137.7S14203.9179E145.2218M0M4714/11/2017 13:33209GPRMC23231.7A3749.25769S14203.917250.1944.914111721GPGGA23137.7S14203.9179E145.2218M0M4714/11/2017 13:33210GPRMC23231.7A3749.25769S14203.917250.1944.914111721GPGGA23137.7S14203.9179E145.2218M0M4714/11/2017 13:33211GPRMC23231.7A3749.25769S14203.917250.1944.914111721GPGGA23137.7S14203.9179E145.2218M0M4714/11/2017 13:33212GPRMC23231.7A3749.25769S14203.917250.1944.914111721GPGGA23137.7S14203.9179E145.2218M0M4714/11/2017 13:33213GPRMC23231.7A3749.25769S14203.917250.1944.914111721GPGGA23137.7S14203.9179E145.2218M0M4714/11/2017 13:33214GPRMC23231.7A3749.25769S14203.917250.1944.914111721GPGGA23137.7S14203.9179E145.2218M0M4714/11/2017 13:33215GPRMC23231.7A3749.25769S14203.917250.1944.914111721GPGGA23137.7S14203.9179E145.2218M0M4714/11/2017 13:33216GPRMC23231.7A3749.25769S14203.917250.1944.914111721GPGGA23137.7S14203.9179E145.2218M0M4714/11/2017 13:33217GPRMC23231.7A3749.25769S14203.917250.1944.914111721GPGGA23137.7S14203.9179E145.2218M0M4714/11/2017 13:33218GPRMC23231.7A3749.25769S14203.917250.1944.914111721GPGGA23137.7S14203.9179E145.2218M0M4714/11/2017 13:33219GPRMC23231.7A3749.25769S14203.917250.1944.914111721GPGGA23137.7S14203.9179E145.2218M0M4714/11/2017 13:33220GPRMC23231.7A3749.25769S14203.917250.1944.914111721GPGGA23137.7S14203.9179E145.2218M0M4714/11/2017 13:33221GPRMC23231.7A3749.25769S14203.917250.1944.914111721GPGGA23137.7S14203.9179E145.2218M0M4714/11/2017 13:33222GPRMC23231.7A3749.25769S14203.917250.1944.914111721GPGGA23137.7S14203.9179E145.2218M0M4714/11/2017 13:33223GPRMC23231.7A3749.25769S14203.917250.1944.914111721GPGGA23137.7S14203.9179E145.2218M0M4714/11/2017 13:33224GPRMC23231.7A3749.25769S14203.917250.1944.914111721GPGGA23137.7S14203.9179E145.2218M0M4714/11/2017 13:33225GPRMC23231.7A3749.25769S14203.917250.1944.914111721GPGGA23137.7S14203.9179E145.2218M0M4714/11/2017 13:33226GPRMC23231.7A3749.25769S14203.917250.1944.914111721GPGGA23137.7S14203.9179E145.2218M0M4714/11/2017 13:33227GPRMC23231.7A3749.25769S14203.917250.1944.914111721GPGGA23137.7S14203.9179E145.2218M0M4714/11/2017 13:33228GPRMC23231.7A3749.25769S14203.917250.1944.914111721GPGGA23137.7S14203.9179E145.2218M0M4714/11/2017 13:33229GPRMC23231.7A3749.25769S14203.917250.1944.914111721GPGGA23137.7S14203.9179E145.2218M0M4714/11/2017 13:33230GPRMC23231.7A3749.25769S14203.917250.1944.914111721GPGGA23137.7S14203.9179E145.2218M0M4714/11/2017 13:33231GPRMC23231.7A3749.25769S14203.917250.1944.914111721GPGGA23137.7S14203.9179E145.2218M0M4714/11/2017 13:33232GPRMC23231.7A3749.25769S14203.917250.1944.914111721GPGGA23137.7S14203.9179E145.2218M0M4714/11/2017 13:33233GPRMC23231.7A3749.25769S14203.917250.1944.914111721GPGGA23137.7S14203.9179E145.2218M0M4714/11/2017 13:33234GPRMC23231.7A3749.25769S14203.917250.1944.914111721GPGGA23137.7S14203.9179E145.2218M0M4714/11/2017 13:33235GPRMC23231.7A3749.25769S14203.917250.1944.914111721GPGGA23137.7S14203.9179E145.2218M0M4714/11/2017 13:33236GPRMC23231.7A3749.25769S14203.917250.1944.914111721GPGGA23137.7S14203.9179E145.2218M0M4714/11/2017 13:33237GPRMC23231.7A3749.25769S14203.917250.1944.914111721GPGGA23137.7S14203.9179E145.2218M0M4714/11/2017 13:33238GPRMC23231.7A3749.25769S14203.917250.1944.914111721GPGGA23137.7S14203.9179E145.2218M0M4714/11/2017 13:33239GPRMC23231.7A3749.25769S14203.917250.1944.914111721GPGGA23137.7S14203.9179E145.2218M0M4714/11/2017 13:33240GPRMC23231.7A3749.25769S14203.917250.1944.914111721GPGGA23137.7S14203.9179E145.2218M0M4714/11/2017 13:33241GPRMC23231.7A3749.25769S14203.917250.1944.914111721GPGGA23137.7S14203.9179E145.2218M0M4714/11/2017 13:33242GPRMC23231.7A3749.25769S14203.917250.1944.9141117  21GPGGA23137.7S14203.9179E145.2218M0M4714/11/2017 13:33243GPRMC23342.7A3749.254464S14203.92220.06247.2141117  17GPGGA23137.7S14203.9179E145.2218M0M4714/11/2017 13:33244GPRMC23343.7A3749.254454S14203.92220.09142.6141117  14GPGGA23137.7S14203.9179E145.2218M0M4714/11/2017 13:33245GPRMC23344.7A3749.254464S14203.92220.13298.1141117  1AGPGGA23137.7S14203.9179E145.2218M0M4714/11/2017 13:33246GPRMC23344.7A3749.254464S14203.92220.13298.1141117  1AGPGGA23137.7S14203.9179E145.2218M0M4714/11/2017 13:33247GPRMC23344.7A3749.254464S14203.92220.13298.1141117  1AGPGGA23137.7S14203.9179E145.2218M0M4714/11/2017 13:33248GPRMC23344.7A3749.254464S14203.92220.13298.1141117  1AGPGGA23137.7S14203.9179E145.2218M0M4714/11/2017 13:33249GPRMC23344.7A3749.254464S14203.92220.13298.1141117  1AGPGGA23137.7S14203.9179E145.2218M0M4714/11/2017 13:33250GPRMC23349.7A3749.254466S14203.92220.081.5141117  17GPGGA23137.7S14203.9179E145.2218M0M4714/11/2017 13:33251GPRMC23349.7A3749.254466S14203.92220.081.5141117  17GPGGA23137.7S14203.9179E145.2218M0M4714/11/2017 13:33252GPRMC23349.7A3749.254466S14203.92220.081.5141117  17GPGGA23137.7S14203.9179E145.2218M0M4714/11/2017 13:33253GPRMC23349.7A3749.254466S14203.92220.081.5141117  17GPGGA23137.7S14203.9179E145.2218M0M4714/11/2017 13:33254GPRMC23353.7A3749.254431S14203.92220.0414.3141117  2EGPGGA23137.7S14203.9179E145.2218M0M4714/11/2017 13:33255GPRMC23354.7A3749.254411S14203.922190.06359141117  11GPGGA23137.7S14203.9179E145.2218M0M4714/11/2017 13:33256GPRMC23355.7A3749.254394S14203.922180.0715141117  2BGPGGA23137.7S14203.9179E145.2218M0M4714/11/2017 13:33257GPRMC23356.7A3749.254387S14203.922180.07359.9141117  19GPGGA23137.7S14203.9179E145.2218M0M4714/11/2017 13:33258GPRMC23357.7A3749.254378S14203.922180.04215.6141117  19GPGGA23137.7S14203.9179E145.2218M0M4714/11/2017 13:33259GPRMC23358.7A3749.254364S14203.922180.09341.5141117  1BGPGGA23137.7S14203.9179E145.2218M0M4714/11/2017 13:34260GPRMC23359.7A3749.254351S14203.922170.07317141117  13GPGGA23137.7S14203.9179E145.2218M0M4714/11/2017 13:34261GPRMC23400.7A3749.254342S14203.922170.11180.4141117  13GPGGA23137.7S14203.9179E145.2218M0M4714/11/2017 13:34262GPRMC23400.7A3749.254342S14203.922170.11180.4141117  13GPGGA23137.7S14203.9179E145.2218M0M4714/11/2017 13:34263GPRMC23402.7A3749.254331S14203.922160.21204141117  1BGPGGA23137.7S14203.9179E145.2218M0M4714/11/2017 13:34264GPRMC23402.7A3749.254331S14203.922160.21204141117  1BGPGGA23137.7S14203.9179E145.2218M0M4714/11/2017 13:34265GPRMC23402.7A3749.254331S14203.922160.21204141117  1BGPGGA23137.7S14203.9179E145.2218M0M4714/11/2017 13:34266GPRMC23405.7A3749.254291S14203.922150.05211.1141117  12GPGGA23137.7S14203.9179E145.2218M0M4714/11/2017 13:34267GPRMC23406.7A3749.254272S14203.922140.09114.6141117  1BGPGGA23137.7S14203.9179E145.2218M0M4714/11/2017 13:34268GPRMC23407.7A3749.254256S14203.922130.06182.2141117  19GPGGA23137.7S14203.9179E145.2218M0M4714/11/2017 13:34269GPRMC23407.7A3749.254256S14203.922130.06182.2141117  19GPGGA23137.7S14203.9179E145.2218M0M4714/11/2017 13:34270GPRMC23407.7A3749.254256S14203.922130.06182.2141117  19GPGGA23137.7S14203.9179E145.2218M0M4714/11/2017 13:34271GPRMC23410.7A3749.254211S14203.922110.07337.7141117  1EGPGGA23137.7S14203.9179E145.2218M0M4714/11/2017 13:34272GPRMC23410.7A3749.254211S14203.922110.07337.7141117  1EGPGGA23137.7S14203.9179E145.2218M0M4714/11/2017 13:34273GPRMC23412.7A3749.254193S14203.92210.19186.4141117  11GPGGA23137.7S14203.9179E145.2218M0M4714/11/2017 13:34274GPRMC23413.7A3749.254188S14203.922090.19358141117  13GPGGA23137.7S14203.9179E145.2218M0M4714/11/2017 13:34275GPRMC23414.7A3749.254169S14203.922090.340.1141117  1EGPGGA23137.7S14203.9179E145.2218M0M4714/11/2017 13:34276GPRMC23415.7A3749.25415S14203.922090.0781.8141117  22GPGGA23137.7S14203.9179E145.2218M0M4714/11/2017 13:34277GPRMC23415.7A3749.25415S14203.922090.0781.814111722GPGGA23137.7S14203.9179E145.2218M0M4714/11/2017 13:34278GPRMC23415.7A3749.25415S14203.922090.0781.814111722GPGGA23137.7S14203.9179E145.2218M0M4714/11/2017 13:34279GPRMC23415.7A3749.25415S14203.922090.0781.814111722GPGGA23137.7S14203.9179E145.2218M0M4714/11/2017 13:34280GPRMC23415.7A3749.25415S14203.922090.0781.814111722GPGGA23137.7S14203.9179E145.2218M0M4714/11/2017 13:34281GPRMC23415.7A3749.25415S14203.922090.0781.814111722GPGGA23137.7S14203.9179E145.2218M0M4714/11/2017 13:34282GPRMC23415.7A3749.25415S14203.922090.0781.814111722GPGGA23137.7S14203.9179E145.2218M0M4714/11/2017 13:34283GPRMC23415.7A3749.25415S14203.922090.0781.814111722GPGGA23137.7S14203.9179E145.2218M0M4714/11/2017 13:34284GPRMC23415.7A3749.25415S14203.922090.0781.814111722GPGGA23137.7S14203.9179E145.2218M0M4714/11/2017 13:34285GPRMC23415.7A3749.25415S14203.922090.0781.814111722GPGGA23137.7S14203.9179E145.2218M0M4714/11/2017 13:34286GPRMC23415.7A3749.25415S14203.922090.0781.814111722GPGGA23137.7S14203.9179E145.2218M0M4714/11/2017 13:34287GPRMC23415.7A3749.25415S14203.922090.0781.814111722GPGGA23137.7S14203.9179E145.2218M0M4714/11/2017 13:34288GPRMC23415.7A3749.25415S14203.922090.0781.814111722GPGGA23137.7S14203.9179E145.2218M0M4714/11/2017 13:34289GPRMC23415.7A3749.25415S14203.922090.0781.814111722GPGGA23137.7S14203.9179E145.2218M0M4714/11/2017 13:34290GPRMC23415.7A3749.25415S14203.922090.0781.814111722GPGGA23137.7S14203.9179E145.2218M0M4714/11/2017 13:34291GPRMC23415.7A3749.25415S14203.922090.0781.814111722GPGGA23137.7S14203.9179E145.2218M0M47


JDavis Nov 15, 2017 09:57 AM

I suggest using the GPS() instruction.

Log in or register to post/reply in the forum.