Im getting values above 360 degrees winddirection, sometimes even above 400 degrees.

This  code is in use :

'User Entered Calculation
Windr = (Windr-220+360)MOD 360
If Windr > 360 Then Windr = Windr - 360
If Windr < 0 Then Windr = Windr + 360
If Windr>=360 Then Windr=0

This is my whole program:

'CR1000'define all angles in degrees not radians
AngleDegrees
'Declare Variables and Units  Dim AirTC_2
  Dim SPkPa
  Dim Twg
  Dim Twpg
  Dim Vpg
  Dim Vp
  Dim SVp
  Dim Twch
  Dim VpgVpd
  Dim Top
  Dim Bottom
  Dim SVpW
  Dim N
  Dim WCTF
  Dim WCWSMPH
Public BattV
Public Windr
Public Temp
Public Vocht
Public Windskm
Public Rain_mm
Public BP_mbar
Public BP_mbar_Change
Public Temp_Change
Public Vocht_Change
Public SlrW
Public SlrkJ
Public Tot24
Public Windskn
Public Beaufort
Public AvgBeaufort
Public MaxBeaufort
Public Windroos As String
Public Windrichting As String
Public Beaufortnaam As String
Public Windsms
Public SinWindr
Public CosWindr
Public AvgSinWindr
Public AvgCosWindr
Public AvgWindr
Public SunHrs
Public PotSlrW
Public RTime(9)
Public SolPos(5)
Public TdC
Public TwC
Public WR_m
Public TotWR_m
Public TotSunHrs
Public WC_CAlias RTime(1)=Year
  Alias RTime(2)=Month
  Alias RTime(3)=DayOfMonth
  Alias RTime(4)=HourOfDay
  Alias RTime(5)=Minutes
  Alias RTime(6)=Seconds
  Alias RTime(7)=Microseconds
  Alias RTime(8)=DayOfWeek
  Alias RTime(9)=DayOfYear
  Alias SolPos(1)=SolarAzimuth
  Alias SolPos(2)=SunElevation
  Alias SolPos(3)=HourAngle
  Alias SolPos(4)=Declination
  Alias SolPos(5)=AirMassUnits SunHrs=hours
Units BattV=Volts
Units Windr=Deg
Units Temp=DegC
Units Vocht=%
Units Windskm=kph
Units Windskn=kts
Units Rain_mm=mm
Units BP_mbar=mbar
Units Windsms=m/s
Units SlrW=W/m^2
Units SlrkJ=kJ/m^2
Units Windroos=String
Units Windrichting=String
Units Beaufortnaam=String
 Units PotSlrW=W/m^2
  Units TdC=Deg C
  Units TwC=Deg C
  Units WR_m=meters
  Units WC_C=Deg C
  Units Year=years
  Units Month=months
  Units DayOfMonth=days
  Units HourOfDay=hours
  Units Minutes=minutes
  Units Seconds=seconds
  Units Microseconds=microseconds
  Units DayOfWeek=days
  Units DayOfYear=days
  Units SolarAzimuth=degrees
  Units SunElevation=degrees
  Units HourAngle=radians
  Units Declination=radians
  Units AirMass=unitless'Define Data TablesDataTable(TableTenMin,True,-1)
DataInterval(0,10,min,0)
WindVector (1,Windskm,Windr,IEEE4,False,0,0,1)
FieldNames ("Windskm,Windr")
Sample(1,Windroos,String)
FieldNames ("Windroos")
Maximum(1,Windskm,IEEE4,False,True)
FieldNames ("MaxWindskm")
SampleMaxMin (1,Windr,IEEE4,False)
Average(1,Temp,IEEE4,False)
FieldNames ("Temp")
Maximum(1,Temp,IEEE4,False,True)
FieldNames ("MaxTemp")
Minimum(1,Temp,IEEE4,False,True)
FieldNames ("MinTemp")
Average(1,Vocht,IEEE4,False)
FieldNames ("Vocht")
Maximum(1,Vocht,IEEE4,False,True)
FieldNames ("MaxVocht")
Minimum(1,Vocht,IEEE4,False,True)
FieldNames ("MinVocht")
Average(1,SlrW,IEEE4,False)
FieldNames ("SlrW")
Average(1,Windsms,IEEE4,False)
FieldNames ("Windsms")
Maximum(1,Windsms,IEEE4,False,True)
FieldNames ("MaxWindsms")
Average(1,Windskn,IEEE4,False)
FieldNames ("Windskn")
Maximum(1,Windskn,IEEE4,False,True)
FieldNames ("MaxWindskn")
Sample (1,AvgBeaufort,IEEE4)
FieldNames ("Beaufort")
Maximum (1,Beaufort,IEEE4,False,True)
FieldNames ("MaxBeaufort")
Sample(1,BP_mbar,IEEE4)
FieldNames ("Baro")
Sample(1,Tot24,IEEE4)
FieldNames ("Tot24")EndTableDataTable(TableOneMin,True,-1)
DataInterval(0,1,min,0)
WindVector (1,Windskm,Windr,IEEE4,False,0,0,1)
FieldNames ("Windskm,Windr")
Sample(1,Windroos,String)
FieldNames ("Windroos")
Maximum(1,Windskm,IEEE4,False,True)
FieldNames ("MaxWindskm")
SampleMaxMin (1,Windr,IEEE4,False)
Average(1,Temp,IEEE4,False)
FieldNames ("Temp")
Maximum(1,Temp,IEEE4,False,True)
FieldNames ("MaxTemp")
Minimum(1,Temp,IEEE4,False,True)
FieldNames ("MinTemp")
Average(1,Vocht,IEEE4,False)
FieldNames ("Vocht")
Maximum(1,Vocht,IEEE4,False,True)
FieldNames ("MaxVocht")
Minimum(1,Vocht,IEEE4,False,True)
FieldNames ("MinVocht")
Average(1,SlrW,IEEE4,False)
FieldNames ("SlrW")
Maximum(1,SlrW,IEEE4,False,True)
FieldNames ("MaxSlrW")
Totalize(1,SunHrs,IEEE4,False)
Average(1,Windsms,IEEE4,False)
FieldNames ("Windsms")
Maximum(1,Windsms,IEEE4,False,True)
FieldNames ("MaxWindsms")
Sample(1,TdC,IEEE4)
   Sample(1,TwC,IEEE4)
   Totalize(1,WR_m,IEEE4,False)
   Sample(1,WC_C,IEEE4)
Average(1,Windskn,IEEE4,False)
FieldNames ("Windskn")
Maximum(1,Windskn,IEEE4,False,True)
FieldNames ("MaxWindskn")
Sample (1,AvgBeaufort,IEEE4)
FieldNames ("Beaufort")
Maximum (1,Beaufort,IEEE4,False,True)
FieldNames ("MaxBeaufort")
Sample(1,BP_mbar,IEEE4)
FieldNames ("Baro")
Sample(1,Tot24,IEEE4)
FieldNames ("Tot24")
Sample(1,PotSlrW,IEEE4)
FieldNames ("PotSlrW")
Average(1,TdC,IEEE4,False)
FieldNames ("Dauw")
Maximum(1,TdC,IEEE4,False,True)
FieldNames ("MaxDauw")
Minimum(1,TdC,IEEE4,False,True)
FieldNames ("MinDauw")
Average(1,TwC,IEEE4,False)
FieldNames ("Nattebol")
Maximum(1,TwC,IEEE4,False,True)
FieldNames ("MaxNattebol")
Minimum(1,TwC,IEEE4,False,True)
FieldNames ("MinNattebol")EndTableDataTable (Test,True,0)
DataInterval (0,1,Sec,0)
Sample (1,BP_mbar,IEEE4)
Sample (1,BP_mbar_Change,IEEE4)
EndTableDataTable (TestTemp,True,0)
DataInterval (0,1,Sec,0)
Sample (1,Temp,IEEE4)
Sample (1,Temp_Change,IEEE4)
EndTableDataTable (TestVocht,True,0)
DataInterval (0,1,Sec,0)
Sample (1,Vocht,IEEE4)
Sample (1,Vocht_Change,IEEE4)
EndTable'Main Program
BeginProg
Scan(1,Sec,1,0)'Default Datalogger Battery Voltage measurement BattV
Battery(BattV)
'Generic 4-20 mA Input measurement Windr
VoltDiff(Windr,1,mV2500,2,True,0,_60Hz,0.18,0)
'Generic 4-20 mA Input measurement Temp
VoltDiff(Temp,1,mV2500,3,True,0,_60Hz,0.05,-65)
'Generic 4-20 mA Input measurement Vocht
VoltDiff(Vocht,1,mV2500,4,True,0,_60Hz,0.05,-25)
'Generic 4-20 mA Input measurement Windskm
VoltDiff(Windskm,1,mV2500,1,True,0,_60Hz,0.081035,-39.9875)
'Generic Tipping Bucket Rain Gauge measurement Rain_mm
PulseCount(Rain_mm,1,1,2,0,0.2,0)
'PTB101B Barometric Pressure Sensor (CSL) measurement BP_mbar
VoltDiff(BP_mbar,1,mV2500,6,1,0,_60Hz,0.184,600)
'CM3 Pyranometer (CSL) measurements SlrkJ and SlrW
VoltDiff(SlrW,1,mV250,7,True,0,_60Hz,1,0)
If SlrW<0 Then SlrW=0
SlrkJ=SlrW*0.04330879
SlrW=SlrW*43.30879
'Calculate Sunshine Hours
    'Get current time
    RealTime(RTime(1))
    'Calculate solar position
    SolarPosition(SolPos(),RTime(),1*3600,51.483169,3.622959,0,BP_mbar,Temp)
    'Calculate potential radiation for time && position (multiply sine of solar elevation angle by solar constant 1373)
    PotSlrW=SIN(SunElevation)*1373
    'If the measured value (W/m^2) is greater than 0.4 * the potential solar radiation (W/m^2)
    'and the sine of the sun elevation angle (degrees) is great than 0.1 (elevation angle of 6 degrees)
    'than it has been sunny for the current scan.
    If SlrW>0.4*PotSlrW And SIN(SunElevation)>0.1 Then
     'Calculate sun hours for scan time in seconds
     SunHrs=1/3600*1
    Else
     'Set sun hours for scan time in seconds to 0
     SunHrs=0
     If PotSlrW<0 Then PotSlrW=0
    EndIf
'User Entered Calculation
Windr = (Windr-220+360)MOD 360
If Windr>360 Then Windr =Windr-360
If Windr <0 Then Windr = Windr+360
If Windr>=360 Then Windr=0
 
'Dew Point and Wet-Bulb calculation prep
    AirTC_2=Temp
    SPkPa=101.325
    SatVP(SVp,AirTC_2)
    Vp=Vocht*SVp/100
    'Dew Point calculation 'TdC'
    DewPoint(TdC,AirTC_2,Vocht)
    If TdC>AirTC_2 Or TdC=NAN Then TdC=AirTC_2
    'Find Wet-Bulb 'TwC'
    Top=AirTC_2
    Bottom=TdC
    For N = 1 To 25
     Twpg=Twg
     Twg=((Top-Bottom)/2)+Bottom
     WetDryBulb(Vpg,AirTC_2,Twg,SPkPa)
     VpgVpd=Vpg-Vp
     Twch=ABS(Twpg-Twg)
     If VpgVpd>0 Then
      Top=Twg
     Else
      Bottom=Twg
     EndIf
     If Twch<0.01 Or N=25 Then ExitFor
    Next
    TwC=Twg
    'Wind Run calculation 'WS'
    'Convert to meters per second if needed and multiply by the scan rate in seconds
    WR_m=Windskm/3.6
    'Wind Chill calculation 'WC_C'
    WCTF=1.8*Temp+32
    WCWSMPH=Windskm*0.621371
    WC_C=35.74+0.6215*WCTF-35.75*WCWSMPH^0.16+0.4275*WCTF*WCWSMPH^0.16
    If WC_C>WCTF Or WC_C=NAN Then WC_C=WCTF
    If WCTF>50 Or WCWSMPH<3 Then WC_C=WCTF
    WC_C=(5/9)*(WC_C-32)   '24 hour running total calculation Tot24
Tot24=Tot24+Rain_mm
If IfTime(24,1440,Min) Then Tot24=0
'24 hour running total calculation TotWR_m
TotWR_m=TotWR_m+WR_m
If IfTime(24,1440,Min) Then TotWR_m=0
'24 hour running total calculation TotSunHrs
TotSunHrs=TotSunHrs+SunHrs
If IfTime(24,1440,Min) Then TotSunHrs=0'Calculate 10 Minute Running Average For Wind Direction
SinWindr = SIN(Windr)
CosWindr = COS(Windr)
AvgRun (AvgSinWindr,1,SinWindr,600)
AvgRun (AvgCosWindr,1,CosWindr,600)
AvgWindr = ATN(AvgSinWindr/AvgCosWindr)
If AvgCosWindr < 0 Then
 AvgWindr = 180 + AvgWindr
ElseIf AvgSinWindr < 0 Then
 AvgWindr = 360 + AvgWindr
EndIf

'PTB101B Barometric Pressure Sensor (CSL) measurement BP_mbar
VoltDiff(BP_mbar,1,mV2500,6,1,0,_50Hz,0.184,600)
PortSet(1,0)
If Test.Record(1,1) > 0 Then
'calculate change for one hour
BP_mbar_Change = BP_mbar - Test.BP_mbar(1,1)
EndIf
'Generic 4-20 mA Input measurement Temp
VoltDiff(Temp,1,mV2500,3,True,0,_60Hz,0.05,-65)
PortSet(1,0)
If TestTemp.Record(1,1) > 0 Then
'calculate change for one hour
Temp_Change = Temp - TestTemp.Temp(1,1)
EndIf'Generic 4-20 mA Input measurement Vocht
VoltDiff(Vocht,1,mV2500,4,True,0,_60Hz,0.05,-25)
PortSet(1,0)
If TestVocht.Record(1,1) > 0 Then
'calculate change for one hour
Vocht_Change = Vocht - TestVocht.Vocht(1,1)
EndIf
'User Entered Calculation
If AvgWindr >= 348.75 AND AvgWindr <= 359.9 OR AvgWindr >= 0 AND AvgWindr <= 11.25 Then
 Windroos = "N"
 ElseIf AvgWindr > 11.25 AND AvgWindr < 33.25 Then
 Windroos = "NNO"
 ElseIf AvgWindr > 33.25 AND AvgWindr < 56.25 Then
 Windroos = "NO"
 ElseIf AvgWindr > 56.25 AND AvgWindr < 78.75 Then
 Windroos = "ONO"
 ElseIf AvgWindr > 78.75 AND AvgWindr < 101.25 Then
 Windroos = "O"
 ElseIf AvgWindr > 101.25 AND AvgWindr < 123.75 Then
 Windroos = "OZO"
 ElseIf AvgWindr > 123.75 AND AvgWindr < 146.25 Then
 Windroos = "ZO"
 ElseIf AvgWindr > 146.25 AND AvgWindr < 168.75 Then
 Windroos = "ZZO"
 ElseIf AvgWindr > 168.75 AND AvgWindr < 191.25 Then
 Windroos = "Z"
 ElseIf AvgWindr > 191.25 AND AvgWindr < 213.75 Then
 Windroos = "ZZW"
 ElseIf AvgWindr > 213.75 AND AvgWindr < 236.25 Then
 Windroos = "ZW"
 ElseIf AvgWindr > 236.25 AND AvgWindr < 258.75 Then
 Windroos = "WZW"
 ElseIf AvgWindr > 258.75 AND AvgWindr < 281.25 Then
 Windroos = "W"
 ElseIf AvgWindr > 281.25 AND AvgWindr < 303.75 Then
 Windroos = "WNW"
 ElseIf AvgWindr > 303.75 AND AvgWindr < 326.25 Then
 Windroos = "NW"
 ElseIf AvgWindr >= 326.25 AND AvgWindr <= 348.75 Then
 Windroos = "NNW"
 EndIf
 


'User Entered CalculationIf Windr >= 348.75 AND Windr <= 359.9 OR Windr >= 0 AND Windr <= 11.25 Then
 Windrichting = "N"
 ElseIf Windr > 11.25 AND Windr < 33.25 Then
 Windrichting = "NNO"
 ElseIf Windr > 33.25 AND Windr < 56.25 Then
 Windrichting = "NO"
 ElseIf Windr > 56.25 AND Windr < 78.75 Then
 Windrichting = "ONO"
 ElseIf Windr > 78.75 AND Windr < 101.25 Then
 Windrichting = "O"
 ElseIf Windr > 101.25 AND Windr < 123.75 Then
 Windrichting = "OZO"
 ElseIf Windr > 123.75 AND Windr < 146.25 Then
 Windrichting = "ZO"
 ElseIf Windr > 146.25 AND Windr < 168.75 Then
 Windrichting = "ZZO"
 ElseIf Windr > 168.75 AND Windr < 191.25 Then
 Windrichting = "Z"
 ElseIf Windr > 191.25 AND Windr < 213.75 Then
 Windrichting = "ZZW"
 ElseIf Windr > 213.75 AND Windr < 236.25 Then
 Windrichting = "ZW"
 ElseIf Windr > 236.25 AND Windr < 258.75 Then
 Windrichting = "WZW"
 ElseIf Windr > 258.75 AND Windr < 281.25 Then
 Windrichting = "W"
 ElseIf Windr > 281.25 AND Windr < 303.75 Then
 Windrichting = "WNW"
 ElseIf Windr > 303.75 AND Windr < 326.25 Then
 Windrichting = "NW"
 ElseIf Windr > 326.25 AND Windr < 348.75 Then
 Windrichting = "NNW"
 EndIf'User Entered Calculation
If Windskm<1 Then
Beaufortnaam = "Stil"
ElseIf Windskm<6 Then
Beaufortnaam = "Zwak"
ElseIf Windskm<12 Then
Beaufortnaam = "zwak"
ElseIf Windskm<20 Then
Beaufortnaam = "Matig"
ElseIf Windskm<29 Then
Beaufortnaam = "Matig"
ElseIf Windskm<39 Then
Beaufortnaam = "Vrij krachtig"
ElseIf Windskm<50 Then
Beaufortnaam = "Krachtig"
ElseIf Windskm<62 Then
Beaufortnaam = "Hard"
ElseIf Windskm<75 Then
Beaufortnaam = "Stormachtig"
ElseIf Windskm<89 Then
Beaufortnaam = "Storm"
ElseIf Windskm<103 Then
Beaufortnaam = "Zware storm"
ElseIf Windskm<117 Then
Beaufortnaam = "Zeer zware storm"
ElseIf Windskm>117 Then
Beaufortnaam = "Orkaan"
EndIf'User Entered CalculationWindskn=(Windskm/1.852)
Windsms=(Windskm/3.6)
If Windskm<1 Then
Beaufort=0
ElseIf Windskm<6 Then
Beaufort=1
ElseIf Windskm<12 Then
Beaufort=2
ElseIf Windskm<20 Then
Beaufort=3
ElseIf Windskm<29 Then
Beaufort=4
ElseIf Windskm<39 Then
Beaufort=5
ElseIf Windskm<50 Then
Beaufort=6
ElseIf Windskm<62 Then
Beaufort=7
ElseIf Windskm<75 Then
Beaufort=8
ElseIf Windskm<89 Then
Beaufort=9
ElseIf Windskm<103 Then
Beaufort=10
ElseIf Windskm<117 Then
Beaufort=11
ElseIf Windskm>117 Then
Beaufort=12
EndIfAvgRun (AvgBeaufort,1,Beaufort,600)
AvgBeaufort = Round (AvgBeaufort,0)
If AvgBeaufort > MaxBeaufort Then MaxBeaufort = AvgBeaufort
CallTable(TableOneMin)
CallTable(TableTenMin)
CallTable (Test)
CallTable (TestTemp)
CallTable (TestVocht)
NextScan