CDM-A108 don't go in sleep mode


Yoann MICHIELIN Aug 25, 2016 03:11 PM

Hi,

I'm using a a CDM-A108 module to do some analog measurments. The module is controled by a CR6 datalogger through the CPI bus.I do measures during 2 minutes, and the scan interval is 10 minutes.

I measured the consumption of the CDM A108 module during the measurments :

- 15,6 mA with peaks at 30 mA during measurents

- 15,6 mA when no measurments are done. It is a lot. This consumption remains the same even when I disconnect everything on the CDM-A108, even the CPI cable (but not the power obviously).

In the CDM-A108 manual if found that the current needed was <1mA during sleep (page 16 of the manual). I suppose that my CDM module don't go in sleep mode when it is not measuring... so here is my question :

How to put the CDM-A108 in sleep mode between measurments ?

I have already updated the firmware of the module but it doesnt change anything. The measurments of the module are OK.

Thank you for your answer,

Faithfully,

Yoann MICHIELIN


JDavis Aug 25, 2016 03:46 PM

I would first check that your program is compiling in Pipeline Mode. Sequential Mode won't allow as much sleep time.

To help beyond that, I would need to see the datalogger program.


Yoann MICHIELIN Sep 2, 2016 10:55 AM

Thank you for your answer.

Unfortunatly I need to compile my code in sequential mode.

I dont undestand why the module cant go in sleep mode when the measurments that the CR6 orders to the CDM-A108 only last 2 minutes and then nothing to do for 8 minutes. Why does the CDM A108 doesnt go to sleep when it does no measurments ? Is there a manner of controlling the CDM-A108 sleep mode ?

I cant send you the whole program beacause it is too long (>3000 lines), but only the subroutine where I do measurments on the CDM A108 :

' Mesures du turbi
Sub mesuresTurbi
        ' Allumage du turbi
        PortSet (PORT_RELAIS_TURBI,1)
        
        ' Attente de la fin du demarrage et du nettoyage
        Delay (0,TEMPO_START_TURBI,sec)
        For i_turbi=1 To NB_MESURES_TURBI     
            ' Mesure de la sortie 4-20mA du turbi    (resistance de 250 ohms)
            CDM_VoltDiff (CDM_A108,1,turbi_mV(i_turbi),1,mV5000,PORT_TURBI,True ,0,50,1.0,0)
            ' Tension mesuree inferieure a 1V = courant inferieur a 4 mA => Erreur
            If(turbi_mV(i_turbi) < 980) Then
                turbi(i_turbi) = NaN
            ' Mesure valide : Conversion tension en turbidite
            Else
                turbi(i_turbi) = (turbi_mV(i_turbi) - 980) * (TURBI_20MA - TURBI_4MA)/(5000-980)
            End If
            ' Tempo entre deux mesures
            Delay (0,TEMPO_TURBI,sec)
         Next i_turbi
         
        ' Statistiques sur les mesures
        AvgSpa(meanTurbi,NB_MESURES_TURBI,turbi())      
    MinSpa(minTurbi,NB_MESURES_TURBI,turbi())
    MaxSpa(maxTurbi,NB_MESURES_TURBI,turbi())
    StdDevSpa(stdTurbi,NB_MESURES_TURBI,turbi())
    AvgSpa(meanTurbi_mV,NB_MESURES_TURBI,turbi())            
    
        ' Extinction du turbi
        PortSet(PORT_RELAIS_TURBI,0)
        
End Sub


JDavis Sep 2, 2016 02:17 PM

You should try putting the analog measurements within Subscans instead of a For loop.