ndonso Jun 14, 2016 04:40 AM

Dear,

If anyone can help i'd really appreciate it.

I'm trying to program the reading of a anemometer 05103 Wind Monitor for CR300 datalogger using CRBasic. According to what I understand speed measurement should be performed in the P_LL port because it is a Low Level AC but when trying to compile says " 8 is not a valid low level AC input port. "

[Version]C:\Campbellsci\Lib\Compilers\CR300Comp.exe VERSION:CR300.Std.01 DATE:3/09/2016
C:\Users\palomo\Desktop\CMRIS\CMRIS_CR300.CR300 -- Compile Failed!

line 51: 8 is not a valid low level AC input port.
Error(s) detected in the program. Double-click an error above to navigate to it.

The program is as follows:

 

'CR300 Series Datalogger

Public PTemp, batt_volt
Public Air_TC
Public RH
Public Rain_mm
Public WS_ms
Public WindDir

DataTable (Min30,1,-1) 
	DataInterval (0,30,Min,0)
	Minimum (1,batt_volt,FP2,False,False)
	Sample (1,PTemp,FP2)
	Average (1,Air_TC,FP2,0)
	Sample (1,RH,FP2)
	Totalize (1,Rain_mm,FP2,0)
	WindVector (1,WS_ms,WindDir,FP2,False,0,0,0)

EndTable

BeginProg
	Scan (1,Sec,0,0)
		PanelTemp (PTemp,60)
		Battery (batt_volt)
    VoltSe(Air_TC,1,mV2500,1,0,0,50,0.1,-40.0)
    VoltSe(RH,1,mV2500,2,0,0,50,0.1,0)
    If (RH>100) AND (RH<108) Then RH=100
    PulseCount (Rain_mm,1,C1,2,0,0.1,0)
    PulseCount (WS_ms,1,P_LL,1,1,0.098,0)'Line that fail(line 51)
    BrHalf (WindDir,1,mV2500,3,Vx1,1,2500,False,20000,50,355,0)
    If WindDir>=360 OR WindDir<0 Then WindDir=0  
		CallTable Min30
	NextScan
EndProg

 Regards


aps Jun 14, 2016 10:07 AM

I am sorry but this was a bug in the first release of the firmware for the logger.

Please go to here:

https://www.campbellsci.com/downloads?c=9999&d=368

And download OS Version 2.   Run the exectuable to update your PC compiler files and to copy the logger firmware onto your PC.  Then upgrade the operating system on the logger with the new version using our Device Configuration Tool.

That should fix the pulse count issue.


ndonso Jun 16, 2016 05:36 AM

Gracias!